    Exadata X2 - power connector in Europe ?

    985510
      Hello ,

      What kind of power connector(s) is(are) required to plug-in an Exadata X2 Quarter-RAC (European version)? And how many connectors ?

      BR.
      C.
        • 1. Re: Exadata X2 - power connector in Europe ?
          damorgan
          Rhetorical question ... What country in Europe?

          Ask your sales rep.
          • 2. Re: Exadata X2 - power connector in Europe ?
            985510
            Hello,

            The country is France.


            Got a not very clear answer from sales rep. :


            "6 power cords for two PDUs, 25 amps at 220/380 - 240/415 VAC 1-phase voltage"


            I really need 6 power cords for a quarter RAC ? Do I need to provide the plugs or the outlets ?

            Thanks a lot,
            C.
            • 3. Re: Exadata X2 - power connector in Europe ?
              robinsc
              this is the cord that will be on the exadata machine http://t.co/cHiFaJPLKE. note that there are two pdus each needing 3 phases hence 6 cords that you need to buy 6 corresponding sockets for. As always the best practise is that pdu a and pdu b should be hooked up to two independant power sources... Ther is another three phase option that only requires 2 power connections. You need to choose which connector is best for you depending on your datacentre setup.
              Picture are in the orifginal exadata site plannig guide. I expect that the owner's mguide should also have them ... I'll check in a little while and let you know.

              Edited by: robinsc on Mar 24, 2013 3:31 PM
              • 4. Re: Exadata X2 - power connector in Europe ?
                LaserSoft
                Hi Friend,

                We have faced same issue last month.

                We understand for a Qtr Rack 4 Sources are sufficient and for Full Rack all 6 are needed.

                This is well documented in *"Owners Guide"* Please refer

                Hope it helps..

                Thanks
                LaserSoft